Welcome to AggreGate Community

Holding & Input registers which type is Read only?

Discussion of AggreGate SCADA/HMI, AggreGate Building Automation and AggreGate Data Center Supervisor products.

Holding & Input registers which type is Read only?

Postby viokast&yahoo.gr » Thu Feb 09, 2017 12:11 pm

Hello all,

In the text (Aggregate Documentation 5.31.15, page=185) :
the Holding registers described as Read-Only registers, and
the Input Registers described as Read/Write registers.

In the Modbus protocol (see modbus.org specification)
this is quite the opposite :
Holding registers : Read/Write,
Input registers : Read only

My question is if the software treats the modbus registers in the way the manual describes,
or the way the modbus protocol defines them (so it is only a mistyping).

Please clarify.

Nikolas
viokast&yahoo.gr
 
Posts: 4
Joined: Thu Nov 24, 2016 10:38 pm

Re: Holding & Input registers which type is Read only?

Postby Anton Logoyskiy AggreGate » Thu Feb 09, 2017 1:33 pm

Hi Nikolas,

Thank you for this notice.

My question is if the software treats the modbus registers in the way the manual describes,
or the way the modbus protocol defines them (so it is only a mistyping).

I'm sorry for this mistypes. Of course second variant is correct.
We fix our documentation soon.

BR/Anton
Tibbo Systems
Anton Logoyskiy AggreGate
 
Posts: 93
Joined: Wed Jul 22, 2015 10:05 am

Re: Holding & Input registers which type is Read only?

Postby junaid.et&gmail.com » Sat May 30, 2020 1:38 pm

In standard Modbus Protocol, the following stands true,
Holding registers (Address 40001,40002 etc) = R/W (Function Code use to Read 3)
Input registers (Address 30001,30002 etc) = R (Function Code use to Read 4)

I hope this helps.
junaid.et&gmail.com
 
Posts: 2
Joined: Sat May 09, 2020 11:27 am


Return to Industrial and Building Automation

Who is online

Users browsing this forum: No registered users and 0 guests